chevyx92
Senior Member
- Location
- VA BCH, VA
A 3P, 120/208V, 40KW, 0.8 PF, 60HZ at 1800 RPM generator has a calculated AMP output of 139A. The generator has a factory installed 150A molded case circuit breaker rated at 100 % in it and comes with an ATS rated for 200A. My question is: Do I size the conductors for the 139A or size them to the 150A breaker? Also why can they install 150A breaker to protect the generator when 139A is the rated output? And if I have to size to the 150A breaker, does that mean I can set a 150A panel with main breaker in it? It's a little confusing because with the 139A output, I wouldn't think you be allowed to have a load rated higher than that. What am I missing?