410.118 Access to Other Boxes

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
410.118 Access to Other Boxes. Luminaires recessed in ceilings, floors, or walls shall not be used to access outlet, pull, or junction boxes or conduit bodies, unless the box or conduit body is an integral part of the listed luminaire.

To comply with above new rule, for the hard ceiling, does anyone know any guides showing how to layout access panel location and panel size? Will this be the architect's job? The arch. asked us for panel location in gypboard ceiling area, thank you.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
410.118 Access to Other Boxes. Luminaires recessed in ceilings, floors, or walls shall not be used to access outlet, pull, or junction boxes or conduit bodies, unless the box or conduit body is an integral part of the listed luminaire.

To comply with above new rule, for the hard ceiling, does anyone know any guides showing how to layout access panel location and panel size? Will this be the architect's job? The arch. asked us for panel location in gypboard ceiling area, thank you.

I believe that it would be an authority having jurisdiction call. As long as you can reach it and work on the box then there should not be an issue. Heck the JB on recessed cans is accessible thru a 6" opening and 4" cans are smaller yet that is allowed.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is a common sense issue because there is no real definition of what will provide adequate access.
 