I understand the idea between clearance between the closet storage space and light fixtures, the part I don't understand is why covered LED fixtures are grouped with incandescent at 12" and fluorescent at 6". Most LEDs (at least Leviton 9860 vs 9850) have a lower wattage and a higher lumen to watt ratio, meaning less heat being generated. If the LED has less heat generated, why does it require a 12" clearance instead of the 6"?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Don't use completely enclosed luminaire.

Use a partially open LED listed for surface mount.
 

mbednarik

Member
Location
central iowa
Occupation
Electrician
Leviton "closet lights" say nothing about being listed for a closet storage space in their documentation. The only fixture I have found specifically listed to be in a closet storage space are the closet hanger rod /light combo's. Do you have an example of a regular LED fixture rated to be in the closet storage space?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I understand the idea between clearance between the closet storage space and light fixtures, the part I don't understand is why covered LED fixtures are grouped with incandescent at 12" and fluorescent at 6". Most LEDs (at least Leviton 9860 vs 9850) have a lower wattage and a higher lumen to watt ratio, meaning less heat being generated. If the LED has less heat generated, why does it require a 12" clearance instead of the 6"?
My guess is because a lot of these requirements are arbitrary.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Do you have an example of a regular LED fixture rated to be in the closet storage space?
Retail LED closet lights are totally enclosed, limited to 12 inches with instructions similar to this:
• This fixture should not be used in areas with limited ventilation or high ambient temperatures
A lighting supplier must source a partially open LED listed for 6 inches in the closet
 