We have a project where the owner wants us to move their high bay LED lights. These are factory cord connected and currently have the outlet above. If i move these fixtures a few feet over, they will no longer be directly below the outlet and i will be in violation of 410.62(c) per the electrical inspector. What is the reasoning that it needs to be directly below the outlet? The cord will be visibly for the entire length and it will not be under strain, just a bay over from its current location.
Just looking for a little more clarification for this requirement and/or if this only applies to new construction projects?
I would like to to justify not moving the outlet if possible.
thanks,