I was taught the intent of this section is to 'thermally isolate' the old 60 degree C knob & tube conductors from new fixtures that require 75-90 degree C conductors. [and this section apparently prohibits the use of NM to accomplish this 'isolation'].
410.64 says 'fixtures installed in recessed cavities in wall or ceilings shall comply with 410.65 thru 410.72'.
What about surface mounted fixtures requiring connection to 75-90 degree conductors? Is there not a 'thermal isolation' requirement for them?...or does this fall to 110.3 'per manufacturers listing'?
410.64 says 'fixtures installed in recessed cavities in wall or ceilings shall comply with 410.65 thru 410.72'.
What about surface mounted fixtures requiring connection to 75-90 degree conductors? Is there not a 'thermal isolation' requirement for them?...or does this fall to 110.3 'per manufacturers listing'?