I couldn't get a clear a answer on this one. Why would a large data center use a 416 volt main feed?
I couldn't get a clear a answer on this one. Why would a large data center use a 416 volt main feed?
I couldn't get a clear a answer on this one. Why would a large data center use a 416 volt main feed?
Yes, but there are no 480V motors in a server!... 480 volt motors might need a buck boost to bring up the voltage, however, it still comes out cost effective.
Yes, but there are no 480V motors in a server!
At a big "server farm" (Data Center) there would typically be a separate service for the facilities loads, the HVAC, lighting, etc. It's substantial in and of itself, but from the MV or HV distribution point, they separate the services with different transformers; the 416Y240V services being dedicated to the server racks for the reasons mentioned (plus better load balancing) and then 480Y277 and/or 208Y120 for the more conventional loads.
Google's Data Center in Oregon. I worked on a much much smaller one here in the Bay Area, but got to tour this one in advance to learn what they expected. I was blown away to be honest, I had no idea how much it takes to facilitate all the porn surfing* that goes on in the world.
Typical Server cell:
View attachment 10946
Data Center:
View attachment 10947
Overall facilities mechanical:
View attachment 10948View attachment 10949
*When you go into the lobby at many of the Google facilities, there is a projector displaying the search terms that people are using all across the world at any given moment, streaming by in an upward scroll (no results, just the stuff people type into the search box). It's hard to read if you are only there for a minute or so, but if they make you wait, your eyes can start to track it enough to read much of it. 90% porn related...
Well, how about "240V wye takes less wire and fewer breaker poles for the same than 240V delta"?Just for clarification, 416 volts, no typo. Thanks for the information. I do disdain the "it's more efficient" answer with no further reason or information.
Just for clarification, 416 volts, no typo. Thanks for the information. I do disdain the "it's more efficient" answer with no further reason or information.
416/240 volts is common in other parts of the world - but is usually at 50 Hz, may or may not have anything to do with why they want this voltage. If the equipment is using primarily 240 volts though you can run line to neutral with all the equipment. 240 volt delta systems are another possible option if all the loads are 240 volts, but would require more copper to supply same load.
Kind of covered what I said... and then someCheck out the link Ron posted in post 6, it is interesting.
Why? Just wondering :blink: While I can not speak for your project, the ones I have done do involve a gain.
> Single pole breakers over doubles= 2x more circuits per panel board, so fewer panels
> Phase and egc wire size is halved
> zero transformer losses, lower electric bill
> no money to spend buying, lifting and installing transformer
> 4 wires for 3 circuits to 6 receptacles over 12 wires 6 circuits for 6 receptacles.
> lower losses on the 208 part
> designed used all over the world for decades no problem.
Using a system with half the voltage is just a waist of copper. I know its a non standard in the US and Canada, but its allowed by the NEC, and wise to implement it.
Why? Just can't sleep at night without the answer. What fun would being ignorant be when this forum is available?:roll:
I couldn't get a clear a answer on this one. Why would a large data center use a 416 volt main feed?