4160 vac wire
working in an older factory with a 4160 feed from the main electrical room to a 600 amp switch then into a 4160/480 transformer (1000kva). Wire is 3-350mcm cu tw and a 4/0 ground wire has a 5000v rating in a 3inc conduit. Does not look like the HV wire I have seen in past
Customer wants to use the wire but increase the tranformer so he can put in a 2000 amp set of switchgear.
Questions
Is this wire allowed and if so what is the ampacity at 4160vac?
Questions
No it is not suitable for MV wiring.
Sounds a lot like what we used to see in older water plants. The wire is rated for 5000volts but the problem is it has no integral neutral. I mainly saw it on 2400volt open delta setups. Some people would mistakenly think that since it was rated 5KV you could use it on 4160 systems. If you are getting a delta secondary from it, it will work but that cable is at least 35 years old and should be replaced.
The wire is not suitable for this voltage. This was changed I think in the 2005 NEC Revision since NEC 2002 had allowed the use of non-shielded cables at 4160V. So, installing non-shielded cables to be operated on a 4160V system is now prohibited.
I read somewhere that one of the concern for this was that when a 5000V non-shielded cable is operated at 4160V, the surface of the cable isn't at zero potential. A standing voltage and current always exists and could under certain conditions be danger to anyone who comes in contact with it.