For all my working life I have meggered 4160 volt motors at 5000 volts,recently I have been hearing this is wrong,is there any proof of this?Will this damage the winding?
I'm no expert on MV motor testing, but NETA ATS-2007 Section 7.15.1 for motors and MTS-1997 Table 10.1 for gear says that 5kV rated equipment should be tested at 2500VDC. They don't show using 5000VDC until the equipment rating is 25kV.Biddles A Stitch In Time is an excellent resource for insulation testing. Test voltage levels are discussed on page 16. I have always tested 4160V motors at 5000V because that was the highest setting on our tester. Our new tester will go to 10KV but that is a little too high according to Biddle.
Thanks for the insight. I must admit I haven't looked into this in detail in a really long time. ATS-2009 Section Section 7.15.1 points to ANSI/IEEE Standard 95. IEEE 95-2002 section 2.2 says this:I'm no expert on MV motor testing, but NETA ATS-2007 Section 7.15.1 for motors and MTS-1997 Table 10.1 for gear says that 5kV rated equipment should be tested at 2500VDC. They don't show using 5000VDC until the equipment rating is 25kV.
I'm no expert on MV motor testing, but NETA ATS-2007 Section 7.15.1 for motors and MTS-1997 Table 10.1 for gear says that 5kV rated equipment should be tested at 2500VDC. They don't show using 5000VDC until the equipment rating is 25kV.