Our main (4160) volt feeders were shut down to reroute them to our facility, when work was complete (splicing new in the middle of old wire approx 11 years old) feeder failed megger test. Contractor brought in a cat 480v 3000a generator and a transformer to step up to 4160v. Connected it to our main at switchgear room. they ran a ground wire (I believe from Generator, worked 27 hours it is a little fuzzy) to our switchgear grounding bar which is bonded to our outside grounding array. When fired up we had strange things happening in one building. t-8's exploding, smoked electronics, etc. told them to shut it down and get generator checked out. left at 9:00am after 27 hrs. called back in by supervisor 5 hrs later, said generator tech had been there and everything checked out fine. wanted us to turn things on. I noticed on way to switchgear room that their grounding lead had been taken off our bar and connected to a ground rod driven in the ground. As we tried to energize our buildings three different 4160v breakers tripped. Left them off and tested them found bad lightning arrestors on two of them and cables meggering bad to the building that blew bulbs etc.
Was this generator improperly grounded at first?
If so could that have caused our problems at the three buildings?
If it didn't cause our problems, why would these show up all of a sudden when we energized?
forgot to mention this is an ungrounded delta feed.
Thanks for any help
Was this generator improperly grounded at first?
If so could that have caused our problems at the three buildings?
If it didn't cause our problems, why would these show up all of a sudden when we energized?
forgot to mention this is an ungrounded delta feed.
Thanks for any help