I havn't delt much with equipment that are rated more than 600V. My question is; How do I size conductors, conduits and overcurrent devices (fuses or breakers) for 4160V Chiller? here are the info I have from the cut sheets:
Motor LRA= 223A
Primary RLA=42.5A
MCA=55A
MOCP=70A
I know the cut sheets indicate all those info but I just need to know if the math is done as the same as the 600V equipment. Also, what table do I need to use to figure out the conductor size (will be run overhead in conduit) for the Chiller. (this is an existing Chiller, 250ton, and will be replaced with a new one, 500ton). The existing cable is 3#2(5kv, EPR,insulated, 1/c.
your response is really appreciated
Motor LRA= 223A
Primary RLA=42.5A
MCA=55A
MOCP=70A
I know the cut sheets indicate all those info but I just need to know if the math is done as the same as the 600V equipment. Also, what table do I need to use to figure out the conductor size (will be run overhead in conduit) for the Chiller. (this is an existing Chiller, 250ton, and will be replaced with a new one, 500ton). The existing cable is 3#2(5kv, EPR,insulated, 1/c.
your response is really appreciated