The San Diego City Inspector has asked me to give him the AIC rating of 2 series rated, and identified 200amp, 208volt (3/O wire) sub-panels, using 42kAIC as the base rate to calculate with. The transformer size and impedence
is unknown, only 42kAIC is given as a starting point. The Power company ( SDGE ) has given the 42kAIC rating of the main disconnect breaker requirements. The sub-panels are 95 and 65 ft away from the Main disconnect. My question is, is there a way to calculate this without the transformer KVA or Z rating if so, how do I do it? Thank you for your help.
Go to this page on Mike Holt's main site.
You will find a free excel fault current calculator that you can download.
since you are supposed to use (for whatever reason) 42,000 amps as the available fault current, that is what you would enter on the first field of the spreadsheet, and leave transformer data blank. By entering the 42000 amps you are disregarding transformer capacity and impedance and telling the sheet that the available fault current at your starting point (presumably the service equipment) is 42000.
Then enter conductor details of the next segment of the circuit. Result will tell you available fault current at the end of the next segment.
Assuming some values I came up with about 15,000 amps available at the end of 65 foot run.
But you and your inspector need to get some things straight on terminology and specifically what is being asked for.
First is there really 42000 available at the service? Who stated 42,000 and why? If you have a 42k rated main that doesn't mean 42 k is what is available it just means that is how much that device was designed to safely be able to interrupt.
If there actually is only 25000 available at the service then the end of the 65 foot run will be even less.
If there actually is 42000 available at the POCO transformer, then you need to plug in service conductors data and figure out what is actually available at the service disconnect. If it were 65 feet of 3/0 conductor - then my result of about 15000 would be what is available at the service equipment.
Some of those details can make a huge difference in what the rating of equipment you use needs to be - as well as can make a huge difference in cost.
Long service lateral can significantly reduce what is available at service equipment compared to what is available at transformer.
Add: some of what I said was a result of the "42000" that was given. That is a fairly common rating tier for such equipment and is probably what rating is being reccommended and not the actual available fault current. With that recommendation the actual value could possibly be anywhere between 25k next lower common rating in many cases and 42k.