Hi guys,
I'm doing the CA work for a water treatment pumping station. Now, I know usually I provide a GFEP/GFP breaker for every heat tracing circuit. However, this is considered an industrial application.
But I'm sure it meets the requirements of both conditions of NEC 427.22. Due to the fact that, it must also have an alarm indication of ground faults.
Now the panel that supplies the heat tracing is 208/120V, 3ph, 4W. Does the GFP have to be on the same panel, or can it be before the step down XFMR?
Also FYI, the water treatment plant is served with MV coming in at 4160V, and is transformed down to 480V via a unit substation.
Thanks,
Patty