430-102 disconnect for controller

Status
Not open for further replies.

kmtaylor

Member
I am designing in an industrial facility. I have a MCC room where the VFD is mounted in the same room however is not in line of sight from the C.B.(lockable type) :confused: that feeds it. Do I need to install a disconnect next to the VFD? Or does 430-102(b) apply?
 
Re: 430-102 disconnect for controller

430.102 Location.
(A) Controller. An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location.
The way I see it if the VFD is the controller it must comply with 430.102(A).

There are two exceptions but there is not enough information to address either.

changed the UBB code from
Code:
 to [quote] so that it will fit the page.
 Charlie
  
  [size="1"][ March 01, 2005, 11:04 AM: Message edited by: don_resqcapt19 ][/size]
 
Re: 430-102 disconnect for controller

kmtaylor,
Most VFD's that I have installed had a disconect built in,this will serve as disconnect required.
frank
 