Please help. Is the rating of the motor disconnect based on the FLA motor nameplate or FLC motor Table 430.250?
Please help. Is the rating of the motor disconnect based on the FLA motor nameplate or FLC motor Table 430.250?
Not entirely correct. For almost all calculations in 430, you use the FLC from the tables NOT the motor nameplate FLC, unless the motor nameplate FLC is HIGHER than that shown in the tables, which will be unlikely.FLC of the name plat on the motor
430.250 references the current equivalent HP rating of the motor
Read section 4.1 of this NECA guide, and keep it handy if doing motor work, it's a great resource.