m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Jan 8, 2017 #1 I'm referring to 430.110.c.3, can we apply this section to fcu (fan coil unit), if yes, would that mean the disconnect rating to be 6xfla ?
I'm referring to 430.110.c.3, can we apply this section to fcu (fan coil unit), if yes, would that mean the disconnect rating to be 6xfla ?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jan 8, 2017 #2 IMO the fan coil unit is part of 430 not 440
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 8, 2017 #3 In one of the classes I attended it was stipulated that a FCU was part of 422.1(F)(1).