J JdoubleU Senior Member Mar 6, 2014 #1 The OCPD can be sized at a higher percentage than conductor sizing. Does this mean you will still have to size the conductors to the OCPD?
The OCPD can be sized at a higher percentage than conductor sizing. Does this mean you will still have to size the conductors to the OCPD?
G Gregg Harris Senior Member Location Virginia Occupation Electrical,HVAC, Technical Trainer Mar 6, 2014 #2 Jakewhis said: The OCPD can be sized at a higher percentage than conductor sizing. Does this mean you will still have to size the conductors to the OCPD? Click to expand... No it does not.