E.g. two motors 50 flc & 100 flc respectivelyI am a bit confused by your question.
430.24 is for conductor sizing and it does not state that overload protection is not required.
Just as for a single motor circuit with a fused disconnect or breaker, the upstream OCPD protects against short circuits and will open under a short before the conductors are damaged.
And the overloads at each motor, either internal or external, will also protect the wires against an overcurrent caused by a failed or overloaded motor.
Tapatalk...
Does it mean the motor overload would protect the feeder? what about the unusual overloads at the feeder independently from the motor branch overload?Just as for a single motor circuit with a fused disconnect or breaker, the upstream OCPD protects against short circuits and will open under a short before the conductors are damaged.
And the overloads at each motor, either internal or external, will also protect the wires against an overcurrent caused by a failed or overloaded motor.
Tapatalk...
You can put the "overload" protection at any point in the circuit and it will provide the "overload" protection for that circuit. The ground fault and short circuit protective device must be at the supply end of the circuit.Does it mean the motor overload would protect the feeder? what about the unusual overloads at the feeder independently from the motor branch overload?
E.g. loosing part of the insulation while installation or maintainance.You can put the "overload" protection at any point in the circuit and it will provide the "overload" protection for that circuit. The ground fault and short circuit protective device must be at the supply end of the circuit.
I don't know what "unusual" overload conditions you are talking about, can you give an example.
E.g. loosing part of the insulation while installation or maintainance.
Or, adding additional cables in one cable tray leading to increased required ampacity.
Ultimately, most of the faults are mistakes by others & our duty how to avoid it.The required ampacity determines how big the conductors are. if that increases, you have to increase the conductor size. there is no way around that.
Ultimately, most of the faults are mistakes by others & our duty how to avoid it.
That would be a short circuit and or ground fault not an overload.E.g. loosing part of the insulation while installation or maintainance.
The fact that you are talking about a motor circuit does not make any difference. If you do something after the fact that changes the ampacity of the conductors, will have to change the size of the conductors or the rating of the OCPD.Or, adding additional cables in one cable tray leading to increased required ampacity.
That has nothing to do with the sizing of the OCPD. It has everything to do with the selection of the wiring method and the installation practices.Ultimately, most of the faults are mistakes by others & our duty how to avoid it.
Don, all of the above posts just to ask how we can protect the feeder against overloads in group of motor combination.That has nothing to do with the sizing of the OCPD. It has everything to do with the selection of the wiring method and the installation practices.
The fact is if we can select between either cable damage or breaker trip of course, we will go for breaker trip.That would be a short circuit and or ground fault not an overload.
The fact that you are talking about a motor circuit does not make any difference. If you do something after the fact that changes the ampacity of the conductors, will have to change the size of the conductors or the rating of the OCPD.
Please read the post that I replied to. It does not appear to me to be to be talking about protection from overloads. The code is clear on how you provide that protection. As others have said the code is the minimum and if you want to exceed the code you are free to do so.Don, all of the above posts just to ask how we can protect the feeder against overloads in group of motor combination.
Compliance with the code rules provides the required protection.The fact is if we can select between either cable damage or breaker trip of course, we will go for breaker trip.