I hope this is a simple question on the approach to elevator motor feeder sizing.
Does one combine the effects of 430.24 (motor feeder circuit = 125% of the largest motor current + sum of other motor currents) with 621.14 (demand factor for elevators).
E.g., so if I have 5 elevators that have currents 20, 10, 5, 5, 3... I'd end up with : 82% * (20 * 125% + 10 + 5 + 5 + 3).
Thx