430.24
dec
Ok..... I have gone over this article many times and still read the quantity 125% and thats great. What I don't understand is .....take several motors say five motors at 10 amps each. Now add them up. 50 amps total. Now take 125% of the largest. 10x1.25= 12.5. Now my total is 62.5 amps. That said... Why am I being told to just add 25% of the largest to the 50 amps to get my total amperage? I've ben told the math is the same- but go figure it yourself. 62.5 is not the same as 52.5.
don_resqcapt19
Illinois
Because that is exactly what the code rule tells you to do. You are taking the largest motor at 125% which is adding 25%. You do not add 125% of the largest as that would be taking the largest motor at 225%.
dec
125% of largest motor + FLA of all additional motors
(10 x 1.25)+10+10+10+10 = 52.5
The 125% already has the 1st motor FLA
Ok.............I see your point. Next time I'll try READING the article especially where it says "other". I just didn't connect the dots to realize it means "additional" motors. Thanks for your help.