430.32(A) 2005 NEC

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Am I reading the new wording correctly. Motor overload protection is not required unless the motor is used in a continuous duty application?
Don
 
Re: 430.32(A) 2005 NEC

see 430.33 then ask again, this might clear it up a little, this is confusing to say the least

[ March 12, 2005, 04:57 PM: Message edited by: jwelectric ]
 
Re: 430.32(A) 2005 NEC

The substantiation for the change specifically said that motors rated for continuous duty and used in non-continuous applications do not require overload protection. There was no panel statement and no comment in the ROC.
 
Re: 430.32(A) 2005 NEC

I don't really see a change from the 2002 to tell you the truth.

Instead of calling the motor a continuous duty motor, they now call the application of the motor as continuous duty.
 
Re: 430.32(A) 2005 NEC

There is a change from ?02 to ?05 codes in 430.32 (D). This change is in the wording and how it is arranged. It still says the same thing just makes it a little clearer. Or at least I think this was the intent of those poor old souls working on the panel.
 
Re: 430.32(A) 2005 NEC

It now says that when the motor is not used in a continuous duty application, that overload protection is not needed. In the 2002 code a motor that was rated for continuous duty applications required overload protection even when it was not used in that type of application.
(A) More Than 1 Horsepower. Each motor used in a continuous duty application and rated more than 1 hp shall be protected against overload by one of the means in 430.32(A)(1) through (A)(4). [2005NEC]
(A) More Than 1 Horsepower. Each continuous-duty motor rated more than 1 hp shall be protected against overload by one of the means in 430.32(A)(1) through (A)(4). [2002NEC]
Don
 