1. 430.52(C)(1) requires motor BC SCGF OCPD rating or setting NOT exceed calculated value with factor given in Table 430.52.
2. However, in Anex D8 example, it does the opposite based on Exception No.1.
Let's say in D8 example, 102A is calculated for BC SCGF OCPD.
According to 1. above, 100A fuse should be selected as it does NOT exceed 102A calculated.
However, in D8 example, 110A fuse is selected based on 430.52(C)(1) exeption No1.
So between 100A and 110A which one is right? and where I get confusion here?
As far as I understand, 1. above requests when doing the calculation, you must NOT exceed the value in the table 430.53, that is Not exceed 300% for nontime delay fuse?
2. However, in Anex D8 example, it does the opposite based on Exception No.1.
Let's say in D8 example, 102A is calculated for BC SCGF OCPD.
According to 1. above, 100A fuse should be selected as it does NOT exceed 102A calculated.
However, in D8 example, 110A fuse is selected based on 430.52(C)(1) exeption No1.
So between 100A and 110A which one is right? and where I get confusion here?
As far as I understand, 1. above requests when doing the calculation, you must NOT exceed the value in the table 430.53, that is Not exceed 300% for nontime delay fuse?