40A c/b is not the next size up from 33.5A.I this sized correctly?
Motor 240 volts 2 horsepower.
Minimum Circuit Ampacity 13.4 amps x1.25= 16.75 #12NM
Overcurrent protection 13.4 amps x 2.5= 33.5 40 amp breaker.
Circuit ampacity is from the tables. It’s a conservative value so if a motor is replaced the BC wires will be large enough.
Yes, 30A would be the max inverse time c/b size, and #14 would be the min. conductor size.Interesting the table has 12 amps for a 230v 2 hp motor
70% efficiency and .69 power factor. You will need to use the actual FLA in this case, not the table value. But as mentioned, a 35 A breaker, I think.
Exception No. 3:
For a listed motor-operated appliance that is marked with both motor horsepower and full-load current, the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating on the appliance nameplate to determine the ampacity or rating of the disconnecting means, the branch-circuit conductors, the controller, the branch-circuit short-circuit and ground-fault protection, and any separate overload protection.
What Code section requires that?70% efficiency and .69 power factor. You will need to use the actual FLA in this case, not the table value.
Agree. The normal way of sizing the conductors is by using the table. But, considering the nameplate amperage is higher than that of the table, the correct sizing should be based on the higher amps! As one is required to set the thermal overload based on the nameplate amps, it is but logical to adjust the conductor size as the protection setting should be lower than the conductor capacity (otherwise, your conductor gets toasted before the TOL trips!.Do you think the NEC covers all possible situations? You would actually size a motor feeder based on the NEC table if the nameplate FLA is higher?
See 430.6 A 1