Need some help resolving a dispute regarding sizing of the overcurrent device for a single motor load. 430-52 states that the overcurrent device "shall not exceed" the calculated value (in this case for a 200hp 480 motor protected by a dual element fuse) of 420A.
Immediately following this is an exception which states that should the calculated value not be a standard fuse/cb size (it isn't)the next higher standard size "Shall be permitted". In the definitions section, "shall be permitted" = allowed but not required.
So, here is the question, regardless of which is advisable, it seems to me that on an odd size for a single motor load, it is permissible to round either up *or* down, as the exception allows you to round up but does not require it, and rounding down prevents you from exceeding the calculated value, thereby staying legal.
I'm having quite an arguement with someone about this point, who insists that you are "required" to round up from an odd size, but I don't see it. Any help or clarification would be appreciated.
-Noxx
-Noxx