DetroitEE
Senior Member
- Location
- Detroit, MI
I've read through 430.62(A), and I'm a little bit confused on what it's saying, specifically when the feeder ground fault/short circuit protection device is a circuit breaker and the branch circuit ground fault/short circuit protection device is a fuse.
Does this article prohibit sizing the branch circuit fuse at 175% the FLA and the feeder circuit breaker at 250% the FLA when serving a single motor? The way I'm reading it, it sounds like the feeder circuit breaker rating cannot exceed the branch circuit fuse rating.
So, in other words, if I have a 480V, 75 HP motor, (FLA is 96A), would it be a violation to install a 175A fused disconnect next to the motor, and a 225A circuit breaker in the distribution panel feeding the fused disconnect?
Does this article prohibit sizing the branch circuit fuse at 175% the FLA and the feeder circuit breaker at 250% the FLA when serving a single motor? The way I'm reading it, it sounds like the feeder circuit breaker rating cannot exceed the branch circuit fuse rating.
So, in other words, if I have a 480V, 75 HP motor, (FLA is 96A), would it be a violation to install a 175A fused disconnect next to the motor, and a 225A circuit breaker in the distribution panel feeding the fused disconnect?