Say you have a feeder supplying just 2 motors, each with an FLC of 40A. Then 430.24 tells you that the feeder conductors need an ampacity of 1.25 * 40 + 40 = 90A. And with 90A feeder conductors, if the feeder OCPD is an inverse time breaker, 430.62 tells you that the OCPD may be up to 2.5 * 40 + 40 = 140A. [Which is not a standard size, and 430.62 does not permit the next size up, so you'd be limited to 125A.]
But nothing in Article 430 overrides 408.36, which has no exceptions for Article 430 applications, right?. So if a 125A feeder OCPD is used, an MLO panelboard that has houses the branch circuit breakers would need a bus rating of 125A, even though the feeder conductors supplying it only need a 90A ampacity? Somehow panelboard busbars are more delicate than wire-type conductors (which you could just tap twice for two separate disconnects with OCPD), or this is just a case of the NEC not covering every corner case?
[I guess in this example, if a 100A OCPD is used, then the downstream OCPD could possibly be omitted, turning the feeder into a branch circuit, under 430.53(B).]
Cheers, Wayne
But nothing in Article 430 overrides 408.36, which has no exceptions for Article 430 applications, right?. So if a 125A feeder OCPD is used, an MLO panelboard that has houses the branch circuit breakers would need a bus rating of 125A, even though the feeder conductors supplying it only need a 90A ampacity? Somehow panelboard busbars are more delicate than wire-type conductors (which you could just tap twice for two separate disconnects with OCPD), or this is just a case of the NEC not covering every corner case?
[I guess in this example, if a 100A OCPD is used, then the downstream OCPD could possibly be omitted, turning the feeder into a branch circuit, under 430.53(B).]
Cheers, Wayne