I’ve got a 480V (motor) schematic showing a 80VA CPT, @ 480VAC/24VAC.
430.72(B)(4) says I can protect the primary with a 500 percent fuse. And secondary protection is not required per 430.72(B)(3). But 430.72(B)(2) states 450.3 “shall be permitted” for protection...so which one is it?