I am assisting our cost dept in pricing out a project, and it's been a long week
.
I am inclined to tell the cost engineer to include replacement of the MTS. Opinions?
- Existing: 40 HP motor (52 FLA), 125 amp breaker, 150 amp rated manual transfer switch, conductor unknown (perhaps #6).
- Upgrade: 75 HP motor (96 FLA), 250 amp breaker, likely #1 conductors.
- Question: Can I keep the 150A MTS?
I am inclined to tell the cost engineer to include replacement of the MTS. Opinions?