430 Motor and 440 AC Load Calculations

Status
Not open for further replies.

DW98

Member
Question about how to include motor and hvac calcs in the panelboard feeder schedules. I'm confused about whether you add 25% for the largest load of a piece of equipment to the fla of the other loads, and then add all the units up. or if you consider all the units together and add only 25% to the largest load.

fla = full load amps, mca = minimum circuit amps.

Example 1: ten rooftop 208V 3PH gas heat/electric cooling rooftop units, fla/mca = 80/100A. Do you use mca*volt*sqrt(3) = 100A*208*1.73 = 36 kva for all units for a total of 360 kva. Or do you only include mca*volt*sqrt(3) for one unit, and fla*volt*sqrt(3) = 28.8 kva for the others for a total of 36 + 8*28.8266.3 kva?

Example 2: Motors: i think i'm clear on motors. Add up all motor fla, and add 25% to largest motor fla

I've created linked excel load spreadsheets and am trying to nail down the formulas
 