Most of the time we use 125 of the motor full load current per 430.22 to determine the size of the motor branch circuit.
Table 430.22(E) has other duty cycle multipliers, for short time, varying duty, and so on, up to 200%.
Under intermittent duty, it lists pumps, and is for a continuous rated motor its 140%.
This is telling me if I take a water pump that runs less than 3 hours I have to size the conductors at 140% of the motor FLC.
How often are motor circuits for pumps sized at 140%?