Nec 2017 section 430 require voltage drop calculation anywhere? I understand elsewhere it stated for information note only however is their a code requirement in 430 not informational note
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
If I am not mistaken Maryland, like many states (including the entire west coast) has it in the Energy code.

Maryland is on the International Energy Conservation Code (IECC)

2018 IECC:
C405.9 Voltage drop in feeders and branch circuits cannot exceed 5%.
 