440.1 Scope.
The provisions of this article apply to electric motor-driven air-conditioning and refrigerating equipment and to the branch circuits and controllers for such equipment. It provides for the special considerations necessary for circuits supplying hermetic refrigerant motor-compressors and for any air-conditioning or refrigerating equipment that is supplied from a branch circuit that supplies a hermetic refrigerant motor-compressor.

COMMENTARY:
Article 440 does not apply unless a hermetic refrigerant motor-compressor is supplied. Article 440 must be applied in conjunction with Article 430.

My question is, does Article 440 apply to an air handler (w/chill water coil) without any hermetic refrigerant motor-compressors installed within the air handler?
 
IMO, No.
Off hand I would think 422 would be the appropriate Article
 
...

My question is, does Article 440 apply to an air handler (w/chill water coil) without any hermetic refrigerant motor-compressors installed within the air handler?
No.

440.3 Other Articles.
...
(B) Articles 422, 424, or 430. The rules of Articles 422,
424, or 430, as applicable, shall apply to air-conditioning
and refrigerating equipment that does not incorporate a hermetic
refrigerant motor-compressor. This equipment includes
devices that employ refrigeration compressors
driven by conventional motors, furnaces with air-conditioning
evaporator coils installed, fan-coil units, remote forced
air-cooled condensers, remote commercial refrigerators,
and so forth.
 