My company is starting a design for a renovation project on an old building, which once was a manufacturing facility. I noticed that the main switchboard and several distribution panels are rated 440 volt. Testing the voltage at a distribution panel confirmed my belief that the voltage was 480 volts (it actually ranged from 487 to 493 volts).
The switchboard and distribution panels are quite old and at one time the facility may have had a 440 volt service.
Our scope of work does not include the replacement of 440 volt equipment, but I will be writing a letter to the owner about my concerns.
I feel that the equipment does not comply with article 110.4 regarding voltages and may be a safety concern. The facility engineer feels that they are “grand fathered”. This can’t be the case since they probably had a 440 volt service at one time.
Has anyone had a similar situation?
The switchboard and distribution panels are quite old and at one time the facility may have had a 440 volt service.
Our scope of work does not include the replacement of 440 volt equipment, but I will be writing a letter to the owner about my concerns.
I feel that the equipment does not comply with article 110.4 regarding voltages and may be a safety concern. The facility engineer feels that they are “grand fathered”. This can’t be the case since they probably had a 440 volt service at one time.
Has anyone had a similar situation?