445.13 Says to size conductors at 115% of name plate. There is an exception when the generator is designed to prevent overloading. The typical residential generator has a circuit breaker. Is this the exception, therefore the conductors can be sized at 100% of name plate?
 

tank728

Senior Member
Location
New Jersey
Occupation
Electrician
Off hand, I believe that rule is stating the conductors from the generator to the first over current protection shall be sized 115%. So in your case the manufacturer has already taken care of this
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
How does the size of the breaker relate to the size of the nameplate?
The specifications state the 22 KW Generac generator comes with a 100 amp breaker. My question, do I size the conductors at 100 amps or 115 amps?
 