For multiple taps of a generator, is it the intent of the code that each set of taps be rated not less than 115% of the generator rating?
Have a situation where an existing generator feeder is not fully rated based on generator capacity, but is undersized to add any more significant load. I want to add a 2nd tap for a fire pump whose required feeder size is also less than the generator capacity. (I've established that the generator can support the entire existing + fire pump load.) An inspector is requiring the fire pump feeder to based on generator rating rahter than pump load rating.
Have a situation where an existing generator feeder is not fully rated based on generator capacity, but is undersized to add any more significant load. I want to add a 2nd tap for a fire pump whose required feeder size is also less than the generator capacity. (I've established that the generator can support the entire existing + fire pump load.) An inspector is requiring the fire pump feeder to based on generator rating rahter than pump load rating.