445.18 Disconnecting Means and Shutdown of Prime Mover

Status
Not open for further replies.
Hello, I am trying to find a definition of 445.18 to explain the following "The revisions to 445.18 now indicate that the remote manual stop cannot be located on the enclosure, so that verbiage is more stringent than NFPA 110. " of https://www.ecmweb.com/national-electrical-code/article/20902695/generator-shutdown-means


445.18 Disconnecting Means and Shutdown of Prime Mover.
(A) Disconnecting Means. Generators other than cord-and-plug-connected portable shall have one or more disconnecting means. Each disconnecting means shall simultaneously open all associated ungrounded conductors. Each disconnecting means shall be lockable in the open position in accordance with 110.25.
(B) Shutdown of Prime Mover. Generators shall have provisions to shut down the prime mover. The means of shutdown shall comply with all of the following:
(1) Be equipped with provisions to disable all prime mover start control circuits to render the prime mover incapable of starting
(2) Initiate a shutdown mechanism that requires a mechanical reset

The provisions to shut down the prime mover shall be permitted to satisfy the requirements of 445.18(A) where it is capable of being locked in the open position in accordance with 110.25.

Generators with greater than 15 kW rating shall be provided with an additional requirement to shut down the prime mover. This additional shutdown means shall be located outside the equipment room or generator enclosure and shall also meet the requirements of 445.18(B)(1) and (B)(2).
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It does not say it cannot be on the enclosure. It only requires it be outside of the enclosure. Both 445.18(C) and (D) say
shall be located outside the equipment room or generator enclosure
I do not see that language as prohibiting the emergency shutdown device from being installed on the generator enclosure.
 