Per 445.18, it strikes me that there is no requirement on where the disconnect required by (A) or the EPO lockable in the open position, required by (B) and which may be utilized in lieu of (A). I know that Articles 700 through 702 require a disconnect within sight of the unit but that wouldn't effect where you put an EPO if you choose to use that EPO in lieu of the disconnect.
So where does that EPO need to be.
Also the last paragraph in (B) (which I think ought to have been (C) requires yet another EPO, and this time it gives a choice of two locations. So it seems to me, to meet the requirements of 445.18 (disregarding the disconnect requirements of 700 through 702), you could put in two EPO's; one lockable open and one not necessarily outside the enclosure of the generator right next to each other.
Is it me, or is this not nailed down as well as it could be?
So where does that EPO need to be.
Also the last paragraph in (B) (which I think ought to have been (C) requires yet another EPO, and this time it gives a choice of two locations. So it seems to me, to meet the requirements of 445.18 (disregarding the disconnect requirements of 700 through 702), you could put in two EPO's; one lockable open and one not necessarily outside the enclosure of the generator right next to each other.
Is it me, or is this not nailed down as well as it could be?