120/208What's the voltage? Is there a neutral?
I like that oneYou have 100 psi in water pressure coming into your home's plumbing system. Having 100 psi at the hot and 100 psi at the cold at the faucet does not make 200 psi.
Can anyone put in layman's terms how to explain to a customer that 2 45 amp fuses that feed a riser does not mean that you have 90a loo
Sent from my SM-G965U using Tapatalk
120/208
Sent from my SM-G965U using Tapatalk
On my hot tub, everything was 240 volt, so I did not need a load neutral, just the line neutral to power the breaker electronics. Probably the same way that one works.
The hot/cold water and rope pull explanations are not 100% analogous to multiwire voltage source though
As mentioned OP can have two 45 amp loads at 120 volts or he can have one 45 amp load at 208 volts.
More confusion for those that don't know how this works - that is 10800 VA total ability at 120 volts but only 9360 at 208. gets more complex when there is combination of 120 and 208 volt loads.
Remember who the audience is for this explanation.
The hot/cold water and rope pull explanations are not 100% analogous to multiwire voltage source though
As mentioned OP can have two 45 amp loads at 120 volts or he can have one 45 amp load at 208 volts.
More confusion for those that don't know how this works - that is 10800 VA total ability at 120 volts but only 9360 at 208. gets more complex when there is combination of 120 and 208 volt loads.
Yes, but still at the original voltage.I would also try to clarify that 2 - 45 amps fused in parallel would be 90.