Situation in a nutshell:
Customer wants to replace a 45 kva transformer with a 75 kva transformer to feed a specific piece of equipment that doesn't require the full output that a 75 kva transformer can provide. After doing a bunch of math, I've come to the conclusion (don't know if it's right) that the current feeder for the 45 kva transformer is still sufficient enough to carry the additional current required by the new piece of equipment.
Details:
The current setup:
3 phase 480V -- 60A breaker -- #6 THHN feeding 45 kva 480v delta 120/208 wye transformer -- secondary feeds 125A breaker disconnect.
Customer is requesting that we:
Keep the same primary (cost savings). 60A breaker with #6 feeders to a 75 kva transformer. The secondary will then feed a 150A breaker disconnect with 1/0 conductors.
Here are the specs for the new equipment that were given to me.
Recommended service amps: 150
FLA: 102
PF: .95
FL KVA: 34.79
FL KW: 33.05
And here's my math.
New equipment FLA 102 x 125% (continuous load) = 127.5A
Secondary math: 127.5A x 208V x 1.73 = 45.8 kva
Primary math: 45.8kva/480v/1.73 = 55.25A (which the 60A breaker and #6 will be sufficient for)
If that math is wrong, and I should actually be using the secondary breaker disconnect rating instead since the conductors should be protected all the way up to 150A, then:
secondary disconnect: 150A x 208V x 1.73 = 53.9 kva
primary math: 53.9kva/480v/1.73 = 65A (which is more than the 60a primary breaker but still good with #6)
The FLA is 102A which is well short of the 150A secondary breaker so I don't think that would be an issue. If there was a problem with the equipment, I would think it will actually trip the 60A primary side breaker before the 150A secondary breaker, and since it's well below the transformer rating, the transformer will still be protected.
Here's my issue:
Any transformer I've ever installed has been to the full rating of the transformer. A primary breaker and conductor sized appropriately and a secondary breaker and conductor sized appropriately for the full use of the transformer. In this situation, the piece of equipment needs slightly over what the 45kva transformer can provide, but not the full nut that a 75kva transformer can provide (which according to the FLA specs, I honestly think it will still work with the 45kva, but they're pushing for the 75kva to be installed). So my question is, is it code compliant to still feed the 75kva with a 60A breaker and #6 conductors even though it's really rated to be fed with 90A. My thoughts are that it's ok because the conductors and equipment are all protected appropriately by it's corresponding breaker. Who cares if I'm not using the transformer to it's full potential as long as what I have installed is protected by a breaker? But, speaking with a fellow contractor, he also has never been in this situation, and his thoughts are that if the primary conductor is undersized according to what's available by the transformer, someone down the road might think it's ok to increase the secondary load assuming the primary feeder is sufficient. Which is very possible, but at that point, the primary 60A breaker should still trip before the #6 gets damaged, right? This might be a common thing for others, but for me and my other contractor friend, we've never had this situation so just want to hear from anyone else if this allowed. I've also seen a few things online about an inrush current when turning the transformer on which can cause the primary breaker to trip if not sized properly. So if that's an issue that people have seen I'll have to keep that in mind as well.
Customer wants to replace a 45 kva transformer with a 75 kva transformer to feed a specific piece of equipment that doesn't require the full output that a 75 kva transformer can provide. After doing a bunch of math, I've come to the conclusion (don't know if it's right) that the current feeder for the 45 kva transformer is still sufficient enough to carry the additional current required by the new piece of equipment.
Details:
The current setup:
3 phase 480V -- 60A breaker -- #6 THHN feeding 45 kva 480v delta 120/208 wye transformer -- secondary feeds 125A breaker disconnect.
Customer is requesting that we:
Keep the same primary (cost savings). 60A breaker with #6 feeders to a 75 kva transformer. The secondary will then feed a 150A breaker disconnect with 1/0 conductors.
Here are the specs for the new equipment that were given to me.
Recommended service amps: 150
FLA: 102
PF: .95
FL KVA: 34.79
FL KW: 33.05
And here's my math.
New equipment FLA 102 x 125% (continuous load) = 127.5A
Secondary math: 127.5A x 208V x 1.73 = 45.8 kva
Primary math: 45.8kva/480v/1.73 = 55.25A (which the 60A breaker and #6 will be sufficient for)
If that math is wrong, and I should actually be using the secondary breaker disconnect rating instead since the conductors should be protected all the way up to 150A, then:
secondary disconnect: 150A x 208V x 1.73 = 53.9 kva
primary math: 53.9kva/480v/1.73 = 65A (which is more than the 60a primary breaker but still good with #6)
The FLA is 102A which is well short of the 150A secondary breaker so I don't think that would be an issue. If there was a problem with the equipment, I would think it will actually trip the 60A primary side breaker before the 150A secondary breaker, and since it's well below the transformer rating, the transformer will still be protected.
Here's my issue:
Any transformer I've ever installed has been to the full rating of the transformer. A primary breaker and conductor sized appropriately and a secondary breaker and conductor sized appropriately for the full use of the transformer. In this situation, the piece of equipment needs slightly over what the 45kva transformer can provide, but not the full nut that a 75kva transformer can provide (which according to the FLA specs, I honestly think it will still work with the 45kva, but they're pushing for the 75kva to be installed). So my question is, is it code compliant to still feed the 75kva with a 60A breaker and #6 conductors even though it's really rated to be fed with 90A. My thoughts are that it's ok because the conductors and equipment are all protected appropriately by it's corresponding breaker. Who cares if I'm not using the transformer to it's full potential as long as what I have installed is protected by a breaker? But, speaking with a fellow contractor, he also has never been in this situation, and his thoughts are that if the primary conductor is undersized according to what's available by the transformer, someone down the road might think it's ok to increase the secondary load assuming the primary feeder is sufficient. Which is very possible, but at that point, the primary 60A breaker should still trip before the #6 gets damaged, right? This might be a common thing for others, but for me and my other contractor friend, we've never had this situation so just want to hear from anyone else if this allowed. I've also seen a few things online about an inrush current when turning the transformer on which can cause the primary breaker to trip if not sized properly. So if that's an issue that people have seen I'll have to keep that in mind as well.