- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
I envision this phrase to mean the area between the structural ceiling and a suspended ceiling, as you might have in an office or retail building. A colleague is designing a project in a waterfront area that will have kiosks for small coffee shops and other vendors. The utility will only provide 480 volts, so the kiosks will need step down transformers. The ceilings will be very high and will include large glass windows in the upper regions. There will be some manner of suspended ceiling above the kiosks, but a person will be able to climb a ladder and walk along catwalks that are above that suspended ceiling, so as to be able to clean the windows. I do not see this as being "hollow," in the context of 450.13. So the 50 KVA limit would not apply.
Anyone care to comment?
Anyone care to comment?