OK, so I am trying to make sense of the 125% rule for primary OCPD and if secondary OCPD is actually required. Application is 50kVA 480v 1P primary, 120/240v 1P secondary, only load is a UPS. UPS is listed at 80A, 240v in, 240v out (nameplate listing) and feeds a single pnl brd, that feeds 6 120vac, 1P, 6A loads (FLA) (all control panels) and LED lighting that is ~240vac at ~7kVA, the lighting has a load shed relay after 1hr all lights connected turn off. Transformer is outside, NEMA 4X, dry type, area is onshore and withing 60 of 70ft of the water and sits on the eastern side of small electrical enclosure where the UPS is installed, moderate rainfall during the year, highs will reach 100 to 105F, never drops below 50F.
The AHJ wants a 100A fused disconnect on the secondary - 125% of the 80A nameplate rating. The design that was permitted was for 100A NF disconnect, to only isolate the UPS when maintenance is needed and of course the client will LOTO the primary CB at the distribution panel as well, the site is only accessible to authorized personnel and is under security monitoring (physical) and operations staff 24/7-365. When operations are tending a vessel, the access is even more closely limited.
So what exactly is the rule for secondary protection? I read 450.3 (B) and it appears that only primary protection is required for I>9A and if secondary I>9A. Am I wrong to pushback on the secondary OCPD (fused disconnect)?
The AHJ wants a 100A fused disconnect on the secondary - 125% of the 80A nameplate rating. The design that was permitted was for 100A NF disconnect, to only isolate the UPS when maintenance is needed and of course the client will LOTO the primary CB at the distribution panel as well, the site is only accessible to authorized personnel and is under security monitoring (physical) and operations staff 24/7-365. When operations are tending a vessel, the access is even more closely limited.
So what exactly is the rule for secondary protection? I read 450.3 (B) and it appears that only primary protection is required for I>9A and if secondary I>9A. Am I wrong to pushback on the secondary OCPD (fused disconnect)?