Not sure I understand... some days I'm slow..some slower
On a delta-wye arrangement you can not rely on the transformer primary protection to protect the secondary conductors. The secondary would need to be protected in accordance with one of the 240.21(C) rules.
IF you have proper primary protection (normally 125%) then your secondary OCP could be based in the conductor requirement only per 240.21(C).
For example, lets say you have a 75 kva 3 phase 480Y/120 arrangement. Your primary protection is say 100 amps.
You can place
(3) 200 amp M/B panels on the secondary and protect the 3/0s. Obviously the secondary protection is far greater than the required transformer protection, however, the transformer is protected by the primary device.
Likewise, if you took the primary protection to 225 amps, then your secondary protection would be limited to 225 amps.
That help ?