450.4 OCPD

Status
Not open for further replies.

PowerdT

Senior Member
Location
San Diego
Occupation
Electrical Engineer
I need some help clarifying Article 450.4 regarding overcurrent protection for the primary.

If I have 1KVA boost transformer 208v primary to 230v secondary and the load is 230V, 14A, 1phase. What size ocpd is acceptable?

Based on 450.4,
1000/(24) * 230v = 9.58kva
9580/230v —> 42A*1.25 gives us about 60A.

However Article 450.4 say, “overcurrent device shall be rated or set at not more than 125 percent of the rated full-load input current of the autotransformer”

Does this mean, ocpd can be rated 20A on primary if my load is only 14A?
 
Yes, 20A is ok. When the Code says "rated full-load input current" they are not referring to the non-autotransformer rating (1,000VA/240V=4.2A). Your 1kVA 240:24V two-winding transformer, when connected as a boosting autotransformer, will be loaded to way less than 1kVA. Only the low-voltage winding carries the full current of the load. So the kVA load on the transformer in your example will be 14A x 24V = 0.336kVA.

The calculation for autotransformer-rated output current is 1000VA/24V = 41.7A. It's autotransformer-rated kVA is 41.7A x 240V = 10kVA and it's input current is 10,000VA / 208V = 48A. So you could us a 48 x 1.25 or 60A breaker, bur the code says "not more than" so 20A is fine.

You could have done the job with a smaller autotransformer.
 
Yes, 20A is ok. When the Code says "rated full-load input current" they are not referring to the non-autotransformer rating (1,000VA/240V=4.2A). Your 1kVA 240:24V two-winding transformer, when connected as a boosting autotransformer, will be loaded to way less than 1kVA. Only the low-voltage winding carries the full current of the load. So the kVA load on the transformer in your example will be 14A x 24V = 0.336kVA.

The calculation for autotransformer-rated output current is 1000VA/24V = 41.7A. It's autotransformer-rated kVA is 41.7A x 240V = 10kVA and it's input current is 10,000VA / 208V = 48A. So you could us a 48 x 1.25 or 60A breaker, bur the code says "not more than" so 20A is fine.

You could have done the job with a smaller autotransformer.
Thank you. Now I am 450.4 expert.
 