I need some help clarifying Article 450.4 regarding overcurrent protection for the primary.
If I have 1KVA boost transformer 208v primary to 230v secondary and the load is 230V, 14A, 1phase. What size ocpd is acceptable?
Based on 450.4,
1000/(24) * 230v = 9.58kva
9580/230v —> 42A*1.25 gives us about 60A.
However Article 450.4 say, “overcurrent device shall be rated or set at not more than 125 percent of the rated full-load input current of the autotransformer”
Does this mean, ocpd can be rated 20A on primary if my load is only 14A?