Greetings! I have an underground electrical service (Single Phase, 200 Amp, 120/240) that I will be installing next week. Here's the problem. The new structure is 500 feet from the existing utility pole. My plan is to install the new 200 amp meter enclosure, 10 feet from the utility pole. I am then installing 450 MCM Aluminum, from the meter to the structure (500 feet) to minimize the voltage loss.
This is my first encounter with 450 MCM Aluminum, (so please pardon my ignorance :?).
Will it comfortably fit in 2-1/2 inch Schedule 40 PVC, and does it comply with NEC code? The utility company did not offer any suggestions, however they strongly recommended that I use the voltage drop calculator, and I did.
I do realize I will have a slight voltage drop due to the distance (about 4% at 150 amps), however, the new structure will only have (6) 8 foot fluorescent fixtures, and roughly (4) 20 amp branch circuits (for work bench receptacles).
Anyone think I will run into issues??
Any help would be greatly appreciated.