450kcmil cable

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Is the next standard size down from what is shown compliant?

Not sure about that. I have 1200A breaker and phase/neutral conductors have been increased to 6 sets of 4#400kcmil AL due to voltage drop

Its confusing to do 250.122(B) with parallel conductors and see if 400kcmil AL would be ok or 500kcmil be ok?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Not sure about that. I have 1200A breaker and phase/neutral conductors have been increased to 6 sets of 4#400kcmil AL due to voltage drop

Its confusing to do 250.122(B) with parallel conductors and see if 400kcmil AL would be ok or 500kcmil be ok?
Is this a feeder or service entrance. If you are using 250.122 i'm assuming feeder in which case you need a 3/0 copper or 250 al. not sure where you are getting 400 for the equipment grounding conductor.

Also, in Post #1 you mention asking about a cable ampacity, but you're referencing 250.22. Not sure which you are concerned with, equipment grounding conductor size or feeder cable ampacity. Post thread is unclear.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Is this a feeder or service entrance. If you are using 250.122 i'm assuming feeder in which case you need a 3/0 copper or 250 al. not sure where you are getting 400 for the equipment grounding conductor.

Also, in Post #1 you mention asking about a cable ampacity, but you're referencing 250.22. Not sure which you are concerned with, equipment grounding conductor size or feeder cable ampacity. Post thread is unclear.

Its feeder fed from 1200A breaker. Their are 6 sets of 4#600kcmil AL Not 4#400 kcmil.

Feeder cable size is increased due to Voltage drop.

250.122(B) would apply and how did you get 250kcmil Al?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not sure about that. I have 1200A breaker and phase/neutral conductors have been increased to 6 sets of 4#400kcmil AL due to voltage drop

Its confusing to do 250.122(B) with parallel conductors and see if 400kcmil AL would be ok or 500kcmil be ok?
Is it 450 kcmil (thread title) or 400 kcmil?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Its 6 sets of 4#600kcmil Al NOT 4#400kcmil
You dind't tell us the wire size to begin with. Please show us your math and we will help you where you are having the problem.

Unless someone else wants to be nice and do it for you first.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
You dind't tell us the wire size to begin with. Please show us your math and we will help you where you are having the problem.

Unless someone else wants to be nice and do it for you first.

I know what the math is. What would be the minimum size conductor for 1200A breaker? How does one determine that to do the math?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
I know what the math is. What would be the minimum size conductor for 1200A breaker? How does one determine that to do the math?
Show us your math if you know it. I have an answer for you and will explain, but I want to know how you got what you got.
 
I know what the math is. What would be the minimum size conductor for 1200A breaker? How does one determine that to do the math?
10 sets of 1/0 AL...... That would be the minimum. But it's not very realistic. Unfortunately the code doesn't tell us how to determine the original/normal size. You just have to pick what you would have used if it wasn't for voltage drop.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Show us your math if you know it. I have an answer for you and will explain, but I want to know how you got what you got.

Very well but you still dont get my point but this should illustrate i know the equation:

1. Lets say you take 3/0 awg AL at 65C then 130A.

1200/130= 9.2 which means minimum 10 sets of 3/0AL req.

3/0 is approx 163kcmil. 163x10=1630kcmil

Using 6 sets of 600kcmil so thats 3600kcmil

3600/1630*250= 552kcmil
 