hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Anyone know if their is such a size cable? Ampacity tables, table 250.122 don’t show it but plans do??
There are some specialty cables that come in "odd" sizes. For example DLO cable comes in a 444 KCMIL, and I believe that is usually also dual rated as RHH for NEC use.
Do they say what type of conductor it is?This for feeder from breaker used as equipment grounding conductor
Do they say what type of conductor it is?
Is the next standard size down from what is shown compliant?
Is this a feeder or service entrance. If you are using 250.122 i'm assuming feeder in which case you need a 3/0 copper or 250 al. not sure where you are getting 400 for the equipment grounding conductor.Not sure about that. I have 1200A breaker and phase/neutral conductors have been increased to 6 sets of 4#400kcmil AL due to voltage drop
Its confusing to do 250.122(B) with parallel conductors and see if 400kcmil AL would be ok or 500kcmil be ok?
Is this a feeder or service entrance. If you are using 250.122 i'm assuming feeder in which case you need a 3/0 copper or 250 al. not sure where you are getting 400 for the equipment grounding conductor.
Also, in Post #1 you mention asking about a cable ampacity, but you're referencing 250.22. Not sure which you are concerned with, equipment grounding conductor size or feeder cable ampacity. Post thread is unclear.
Me neither, although it does depend what is used for the "normal size". Perhaps OP can show the math.not sure where you are getting 400 for the equipment grounding conductor.
Is it 450 kcmil (thread title) or 400 kcmil?Not sure about that. I have 1200A breaker and phase/neutral conductors have been increased to 6 sets of 4#400kcmil AL due to voltage drop
Its confusing to do 250.122(B) with parallel conductors and see if 400kcmil AL would be ok or 500kcmil be ok?
Me neither, although it does depend what is used for the "normal size". Perhaps OP can show the math.
Damnit, I want my money back. I just wasted several minutes on incorrect numbers please send guaranteed funds such as money order or certified check....Its feeder fed from 1200A breaker. Their are 6 sets of 4#600kcmil AL Not 4#400 kcmil.
Feeder cable size is increased due to Voltage drop.
250.122(B) would apply and how did you get 250kcmil Al?
You dind't tell us the wire size to begin with. Please show us your math and we will help you where you are having the problem.Its 6 sets of 4#600kcmil Al NOT 4#400kcmil
Damnit, I want my money back. I just wasted several minutes on incorrect numbers please send guaranteed funds such as money order or certified check....
You dind't tell us the wire size to begin with. Please show us your math and we will help you where you are having the problem.
Unless someone else wants to be nice and do it for you first.
Show us your math if you know it. I have an answer for you and will explain, but I want to know how you got what you got.I know what the math is. What would be the minimum size conductor for 1200A breaker? How does one determine that to do the math?
10 sets of 1/0 AL...... That would be the minimum. But it's not very realistic. Unfortunately the code doesn't tell us how to determine the original/normal size. You just have to pick what you would have used if it wasn't for voltage drop.I know what the math is. What would be the minimum size conductor for 1200A breaker? How does one determine that to do the math?
Show us your math if you know it. I have an answer for you and will explain, but I want to know how you got what you got.
….You just have to pick what you would have used if it wasn't for voltage drop.