kchap
Member
- Location
- Peculiar, MO, USA
Showing my ignorance in regard to power circuits here... A customer had me build a control panel for some equipment that includes five motors with a total load of about 100 Amps, with the largest motor load being a 20 HP. The supply power is 208V. After the fact, the customer realized that the 20 HP motor is rated for only 480V, and the others are rated 240/480V. So he got with his electrician and came up with a solution that involves splitting the 208V downstream from the feeder circuit OCPD. Two motors will remain on 208, and then they will install a 45kVA transformer to step up to 480V for the other three motors. Should the secondary side of the transformer be treated as a feeder circuit, requiring a main breaker in addition to three breakers for the motors? If yes, I assume it should be sized according to UL 508A, section 32.3. Would that be correct?