45kVA transformer protection

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Saw a print has a 45kVA xfmr (480V Pri-208/120V Sec) with 70A primary CB in upstream 480V panel that powers the xfmr,
xfmr feeds 208Y/120V panel with 175A main CB. I think the xfmr is protected by its primary 70A CB, but is it something wrong
with 175A main CB in downstream panel? I typically saw 150A main CB panel fed out of a 45kVA xfmr.

80% x 175A = 140A which exceeds xfmr FLA at 45kVA @208/3 (i.e. 125A)
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Saw a print has a 45kVA xfmr (480V Pri-208/120V Sec) with 70A primary CB in upstream 480V panel that powers the xfmr,
xfmr feeds 208Y/120V panel with 175A main CB. I think the xfmr is protected by its primary 70A CB, but is it something wrong
with 175A main CB in downstream panel? I typically saw 150A main CB panel fed out of a 45kVA xfmr.

80% x 175A = 140A which exceeds xfmr FLA at 45kVA @208/3 (i.e. 125A)
IMHO.... down streams are sized to the load. I would say that in this case, the secondary OCPD is too large.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The primary protection meets the 125% rule so the transformer is protected.
From that standpoint the secondary protection is irrelevant as long as the conductors are sized to the secondary OCP
 
The primary protection meets the 125% rule so the transformer is protected.
From that standpoint the secondary protection is irrelevant as long as the conductors are sized to the secondary OCP
Just a reminder to the OP, the secondary device may be doing three things: 1. Transformer secondary protection (450.3), 2. Transformer secondary CONDUCTOR protection (240.21(C)), 3. Panelboard protection (408.36). As Augie said, due to the primary protection, you do not need transformer secondary protection, but you can evaluate what that secondary device is doing for #'s two and three.
 

anbm

Senior Member
Location
TX
Occupation
Designer
Just a reminder to the OP, the secondary device may be doing three things: 1. Transformer secondary protection (450.3), 2. Transformer secondary CONDUCTOR protection (240.21(C)), 3. Panelboard protection (408.36). As Augie said, due to the primary protection, you do not need transformer secondary protection, but you can evaluate what that secondary device is doing for #'s two and three.
Not issue with #2, for #3, brekaker is kind of large vs. transformer FLA, my two cents.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Your two-cents is on target but it is allowed by NEC. IF the primary breaker was any larger then it would be a violation.
Unsure why they would use a 175 unless it was "whats available"... it's too large for the 45 kva and too small for the next standard size (75)
 

jap

Senior Member
Occupation
Electrician
Looks like they're using 125% on both the primary and secondary.

Pretty common.

54 x1.25= 67.50 next size up 70 amps
124.65 x 1.25=155.81 nex size up 175 amps

JAP>
 