I have a 45kva transformer. Delta to wye. Sizing the primary and secondary conductors the engineer is calling for:
Primary: 4awg and 70amp ocpd
Secondary: 1/0awg and 150 ocpd
Shouldn’t the secondary conductors be 2/0 awd if:
45000/208x1.73
Furthermore does derating at 80% come into play with a 4 wire secondary?
Thanks,
Ronnie