dogleg
- Lock haven pa
- Electrician
Good morning, sorry for any rule breaks its been years since posting here. I have a 200 hp compressor motor fed from a 200hp soft starter cabinet. There is 1 disconnect between soft starter and motor . Disconnect is a few feet from each compressor. The picture is the name plate for the 200 hp motor. It's a 12 tap single Voltage motor. It came with the taps set up in delta run configuration. So that is how I connected my 350 kcmil via crimp lug and nut and bolt. My concern is that when I measured resistance between legs on load side of disco with it open the resistance is very lol. When testing my meter leads I get about 0.2 ohms. Also I get the same between all phases on load side of disco which leads me to believe resistance is basically 0 ohms. I have 2 of these compressors and both read the same. I megged between motor casing/egc and each phase and get 2.2 gig which is max for my fluke. So if the resistance between windings is indeed zero ohms does this indicate a problem? I was expecting to see slightly higher resistance. There are no anomalies between different phases they all read same resistance. These mtrs are brand new. I checked taps before connecting they all matched name plate diagram all the way to the right for delta-run. Any thoughts from the large brains in here would be appreciated. Sorry for slang and punctuation if any. Entering this via mobile phone. Thanks
Sent from my SM-F926U1 using Tapatalk