Would be very interested in your collective opinion on this:

I am replacing a 47 year old indoor unit substation with a new outdoor pad mounted transformer AND new indoor main switchboard albeit in a different location for a 90,000 square foot, 4 story college dormitory. So in a not entirely atypical fashion, we will install the new switchboard, run new conduit to the old switchboard. When everything is ready to go with the new, the contractor will de-energize and gut the old switchboard leaving the shell as a junction point.

Now here's my question. I have two options at that point. 1. pull all of the feeders some of which must run hundreds of feet to the various panelboards in this facility and replace them with new in the same conduits OR 2. Splice new conductors to these 47 year old circuits within the shell of the old switchboard.

On the one hand, I am terrified at the unknown factor of directing the contractor to pull these out. What if there is rusting of the conduit and they're stuck. What if he damages them in the process and then we need to run an entirely new feeder and because of the construction, the new feeder would have to be exposed making the people in charge of the dormitories very unhappy.

I lean towards leaving the 47 year old conductors. Do you agree that this is the best of my two options here?

Thanks,

Mike
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I wonder how testing them today is going to ensure that they last another 20 years. If the conduits are in such poor condition that the feeders may not come out then it's possible that the feeders will fail sooner than later. I would pull them out.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If you suspect that there may be hardened waxy lube in the conduits, Polywater (TM) Cable Free (TM) dissolves that stuff and lubricates too.
 
I wonder how testing them today is going to ensure that they last another 20 years.
It won't, but neither will new wire guarantee that (it is likely that new wire will last a long time).

If the conduits are in such poor condition that the feeders may not come out then it's possible that the feeders will fail sooner than later. I would pull them out.
Nothing says they are in bad condition, they could be fine. And we've probably all seen 10 year old wire almost glued in place.

It's kind of a tossup to me-
Maybe you pull out good wire but mess up the pipes.
Maybe you leave tested-good wire and something fails in a year.

What's the cost to replace all the feeders? That's likely the determining factor.
 
Last edited by a moderator:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Hire a contractor qualified to test them and if okay, leave them and splice. If bad then replace.

Perhaps submit test report with indemnity notice of "No Warranty", stating failure of existing equip. can't be warranted.

Then attach 2 estimates to replace feeder & raceways:
1) Most efficiently designed cost, during remodel, and before feeder terminations.
2) Least efficient method of emergency repairs, after unforeseeable failures.
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
Hire a contractor qualified to test them and if okay, leave them and splice. If bad then replace.

My opinion:
Let the owner decide the acceptable level risk they want to take and advise them of the relative cost of both scenarios, as Tony S suggested.

I would at least have a third party do non destructive tests on the conductors and generate a report stating they can be reused. Test them before you do anything else to establish a baseline. Then test them when you are done. Submit both reports and let the design engineer determine that they are acceptable. Explicitly do not warranty the existing feeder conductors.

How much copper (or aluminum) to replace are we talking, relative to the entire project?
 

Fulthrotl

~Autocorrect is My Worst Enema.~
I lean towards leaving the 47 year old conductors. Do you agree that this is the best of my two options here?

Thanks,

Mike

i'd megger all the old feeders AT THEIR WORKING VOLTAGE FIRST,
to see what kind of resistances you are getting, phase to phase, and
phase to ground.

if it all looks good, megger at 1,000 volts. if it still looks good,
i'd hypress butt splices and cold shrink. and reuse them.

pulling them out, in my experience, isn't going to go well. IF you
can get them out at all. polywater makes a lube you pour into the
pipe WELL BEFORE attempting the removal. it'll soften up old wax
lube, etc. like a couple weeks or more before attempting.

something to consider is polywater will migrate thru the entire conduit system.
wonderful if it's an underground run. if it is overhead, expect a pail of the
crap draining into the gear. that doesn't always turn out well, either.

your big downside is damaging the existing stuff in place, rendering it
unusable, and irreplaceable if you can't pull it out. then you have an
exended interruption of service, while stuff is repiped.
 