Re: 48 circuit panel
It took me a while to realize there is a definition for a "lighting and appliance" panelboard. In case this is new to anyone else:
408.14(A) Lighting and appliance branch-circuit panelboard. A lighting and appliance branch-circuit panelboard is one having more thatn 10 percent of its overcurrent devices protecting lighting and appliance branch circuits.
The handbook goes on to explain that the 10 percent applies to 15,20, or 30 amp circuits with a neutral conductor. So if the panel is all three phase breakers, I guess the 60 circuit panel can be used.
I also find it interesting that one manufacturer's rep. stated that a sub feed breaker doesn't count when it is a substantially different size than the other breakers. In other words, he said a panel with 42 branch circuits and a 100A sub feed breaker was acceptable. I'm not sure where he got that from.
Steve